Results 1 to 11 of 11
    Trey Humphreys's Avatar
    Trey Humphreys Guest
    Default ABS Flue Pipe on LP Water Heater
    Never seen this. Granted, I have only performed about 150 inspections but...
    I have seen high efficiency furnaces / boilers with PVC exhaust but never a water heater with ABS... See photo. Any reason this is not acceptable? Also the entire set up is in a basement and the abs has about a 15' horizontal run before it daylights. It is fan assist exhaust but ABS?
    (Please ignore extension chord...entirely different issue.)
    Default Re: ABS Flue Pipe on LP Water Heater
    Quote Originally Posted by Trey Humphreys View Post
    Can't say I have ever seen it either. ABS is not approved for any type of gas appliance that I'm aware of.
    Richard Moore's Avatar
    Richard Moore Guest
    This from a Rheem page at http://waterheating.rheem.com/Docume...PVGuardian.pdf
    Flexible Venting
    Options
    Long venting lengths up to 100 feet
    PVC, ABS, or CPVC vent pipe options
    Vertical or horizontal termination
    (my red)
    Gotta say I would be doing a double-take too, but it seems it is OK.
    I just looked up that same link. Surprise of the day!
    WOW! I agree... Surprise of the day!
    Thanks!
    Colorado Springs, CO
    I learn something every day.
    Bruce Breedlove
    www.avaloninspection.com
    Martin lehman's Avatar
    Martin lehman Guest
    I see them all the time out here on new construction.
    Question Re: ABS Flue Pipe on LP Water Heater
    Sorry guys, I didn't take a picture of this one, but the basic question is whether PVC is considered a combustible material.
    I was in a 50 year old house today. It had a one year old water heater in the basement using the original venting. Single wall vent up to about a foot from the floor where it changed to a type B vent that had about an inch of clearance to the wood. No problem.
    Somewhere in time the owners installed a high efficiency furnace next to the water heater and the PVC furnace combustion air intake passes about one inch away from the single-wall section of the water heater vent.
    I have been looking for combustibility of PVC and the best info that I have found states that it will ignite at somewhere between 390 and 540 degrees (150 - 300 degrees higher than wood). What is considered "combustible"?
    I had a very understanding buyer and we wgreed to both go away and do some research.
    thank you for any help
    Orlando, FL
    PVC is combustible, but stop worrying about the temperature it burns, and start looking at clearances.
    Single wall vent pipe has a much higher clearance requirement. Tables are listed online.
    Dom.
    Mar 2012
    Lansdale, PA
    Its been a long time, but I think I have seen ABS on some of the very early direct vent water heaters. I also recall seeing black corrugated plastic tubing, which was supplied by the manufacturer-not a DIY installation.
    As with all combustion appliances, get the make and model then look up the manual for answers on suitability of materials.
    As for clearances to combustibles, ALL polymeric pipe and venting should be treated as combustible since they cannot pass ASTM E-136. The stated clearance off single walled unlisted vent connector is 6". That includes foam insulation attached to water pipes btw.
    The power vented water heater with the integral draft hood is one of the most dangerous combustion appliances you can find due to its propensity to spill CO. Aside from it spilling CO, note that mess of red RTV silicone where it connects to the appliance collar. What a mess!
    ABS has a higher service temp. than PVC but neither is listed for use as gas combustion venting in the US. It is a conundrum with the codes, which require all venting for positive flue gas pressure to be listed only to look the other way when an appliance mfr. states it's ok to use plastic venting.
