    Default MSE & service-disconnect before or after Meter?

    I inspected an 'upgraded' 1954 Tri-plex the other day. It has an overhead service-drop from a transformer at the back alleyway. The owner recently installed a new MSE (mains cabinet) that was padlocked so I couldn't get inside. It appears the incoming service entrance conductor pathway goes from the weatherhead to the MSE cabinet, into a wire trough, down to 3 individual meter-bases, then through 3 old abandoned 'disco' boxes under each meter, back up to the wire-trough and then into one of three conduits that run up to a gable wall above the MSE and then into the attic and then drop from the attic down to each apartment's subpanel. Got all that!? In my 45 years here in southern Nevada, I don't recall ever seeing the meter 'after' the MSE cabinet or service disconnect. Here are the problems I'm seeing:

    1. No City of Las Vegas inspection tag on the new MSE cabinet.
    2. No approval tag from the POCO (NV Energy) on the MSE cabinet
    3. Disco's before meter instead of 'after'
    4. Using the old meter 'disco' box as a 'pass-thru' and the list goes on.

    Am I missing something else important here...or do I basically have it right? This looks like the owner hired an electrician to install a new MSE cabinet without 'permits' and the POCO inspection and put the 'disco's in the wrong order on the path from service-drop to subpanels.

    Your thoughts?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Glenn R. Curtis CMI
    La$ Vega$, Nevada
    Inspecting Nevada since 1982

  2. #2
    Join Date
    Jul 2008
    Location
    La$ Vega$, Nevada
    Posts
    53

    Default Re: MSE & service-disconnect before or after Meter?

    They cut the padlock off early this morning so I went back and took photo's with trough & main panel covers 'off'. Here's the photo...

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Glenn R. Curtis CMI
    La$ Vega$, Nevada
    Inspecting Nevada since 1982

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: MSE & service-disconnect before or after Meter?

    Glenn, no photos are showing, and without them, and with the lack of other information (because it was locked), I can only ask some questions.

    IF ... if the service entrance conductors go to the new service equipment panel and to a main service disconnect in it, then that would be the main service disconnect for the service. However, each structure (each one of the tri-plex is its own structure, unless it was treated as one structure back in 1954 ... and what the AHJ allowed or what code they were following back is not known), each structure is supposed to have its own service and service disconnect.

    The new service equipment panel would be the change from service entrance conductors to feeders conductors. and not knowing how the new service equipment panel is wired (no photos to look at) ... there are questions, which may not be relevant to what is actually there.

    See if you can upload the photos as that would at least provide a starting point.

    - - - Updated - - -

    Glenn, no photos are showing, and without them, and with the lack of other information (because it was locked), I can only ask some questions.

    IF ... if the service entrance conductors go to the new service equipment panel and to a main service disconnect in it, then that would be the main service disconnect for the service. However, each structure (each one of the tri-plex is its own structure, unless it was treated as one structure back in 1954 ... and what the AHJ allowed or what code they were following back is not known), each structure is supposed to have its own service and service disconnect.

    The new service equipment panel would be the change from service entrance conductors to feeders conductors. and not knowing how the new service equipment panel is wired (no photos to look at) ... there are questions, which may not be relevant to what is actually there.

    See if you can upload the photos as that would at least provide a starting point.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: MSE & service-disconnect before or after Meter?

    This site doesn't work very well most of the time. It eventually allowed my reply to go through, but only after multiple error messages.

    I'll check back in a few days to see if you are able to upload photos, and to see it is is working better then than it is not working well at all now.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Orlando, FL
    Posts
    1,593

    Default Re: MSE & service-disconnect before or after Meter?

    Quote Originally Posted by Jerry Peck View Post
    This site doesn't work very well most of the time.
    Agreed, I often can't get past the server errors to get to the posts.