Results 1 to 29 of 29
  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default Weep hole diameter

    Last edited by Jeff Eastman; 12-19-2007 at 08:52 PM.
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Weep hole diameter

    Possible entryway for insects and vermin. But my main concerns would be: 1) Is that "masonry" extending below grade and parged with mortar? (In any case, insufficient clearance from grade?) Why someone "retrofitted" the weeps in the first place - I would assume there was likely to have been a water problem, or they would not have bothered - and what damage may have resulted. 3) Damage to the flashing (if any) / weather-resistant barrier (house-wrap) / sheathing behind the brick the weeps were installed.


  3. #3
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Weep hole diameter

    And... it these were indeed retro-fitted (a high possibility), that would mean that the hole (only) was installed and there is no flashing in the drain plane.

    Rich


  4. #4
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Weep hole diameter

    Installing "weep-holes" after a masonry wall is built can often cause more problems than not. Hey Clyde, where's my drill?

    Jerry McCarthy
    Building Code/ Construction Consultant

  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Weep hole diameter

    "No flashing in the drain plane..."

    This flashing may not be present:

    http://www.luckstone.com/arch/downlo...onryVeneer.jpg

    http://www.luckstone.com/arch/downlo...onryVeneer.jpg


  6. #6
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    Jeff,
    Where did you get a maximum of 3/8ths? From 2006 IRC R703.6 Weepholes: Weepholes shall be provided in the outside wythe of masonry walls at a maximum spacing of 33 inches (838mm) on center. Weepholes shall not be less than 3/16inch (5mm) in diameter. Weepholes shall be located immediately above the flashing. , so if you have one, I'll appreciate knowing it.
    It wouldn't be unusual for me to miss another reference.
    In any event, I would be concerned with damage to the substrate and flashing (if present) in which case you've just made a direct path to the interior.
    Were you able to identify the debris seen on the grass and foundation? Was that actually stone and mortar or was it shaved stone embedded into a thin layer of concrete over EPS. I know you were there and I'm looking at a picture. I'm just curious because of all the debris.

    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  7. #7
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Weep hole diameter

    Thom,

    I could be wrong (again) but, I think that is water driplets on the grass/ ground.

    RR


  8. #8
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    That's what I originally thought, but look on the foundation and inside the hole.

    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  9. #9
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Weep hole diameter

    Quote Originally Posted by Warren Alderman View Post
    Nothing wrong with retrofitting weep holes, I recommend it all the time.... just make sure to recommend a qualified contractor do it.

    Richard,

    "No flashing in the drain plane"?

    What do you exactly mean?
    Well that recommendation is not very good if the wall is not flashed properly and the air space is full of mortar, or their is not air space. If they are not installed during the construction of the wall it is very doubtful that they will do any good if they are put in post construction.

    Warren, all brick veneer walls should have through wall flashing.

    I would not tell a client to have weeps installed post construction, simply because I have seen post construction weeps that do not work. You have to understand how the wall is constructed and then you will understand why they seldom work if they are installed post construction.

    Last edited by Scott Patterson; 06-01-2007 at 12:47 PM.
    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  10. #10
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Weep hole diameter

    This is what I said two days ago on a 12 year old home that did not have any weep holes.

    "I did not find any weep holes in the brick veneer walls. Weep holes are an important part of the brick veneer wall system. They help air to circulate through the walls and help moisture in the walls to dissipate. Weep holes need to be installed during the construction process for them to work properly.

    I did not see any moisture problems with the home that I could link to the lack of the weep holes. This is not uncommon in the South but it does not mean that future moisture problem could arise due to the lack of the weep holes."


    This is what I typically end up writing about the lack of weep holes. It changes from home to home but this is my common verbiage.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  11. #11
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    Quote Originally Posted by Jeff Eastman View Post
    So do you guys do what Dan suggest, just note the lack of weep holes or just not comment on it?
    Jeff,
    There is never a case I can think of where I would not comment on it. My canned comment is similar to Scott's and gets modified as necessary.
    In most cases, even when they're present, you will not be able to tell if they are functioning. But you will have cases where you can definitely tell when they are not.

    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  12. #12
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Weep hole diameter

    Quote Originally Posted by Jeff Eastman View Post
    Thanks , Scott! That rocks!

    For new construction though, you tell builder to install if they don't put them in, right?
    Even on new construction I do not tell them to put in weeps after the fact. The main reason is that I don't want to be held responsible if they do not work and I told them to install them.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  13. #13
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Weep hole diameter

    Quote Originally Posted by Warren Alderman View Post
    Nothing wrong with retrofitting weep holes, I recommend it all the time.... just make sure to recommend a qualified contractor do it.
    West Coast Jerry nailed it with "Installing "weep-holes" after a masonry wall is built can often cause more problems than not. Hey Clyde, where's my drill?"

    You ever looked inside one of those holes?

    Typically, they drill right through to the siding, past the weather resisting membrane and the paper, right through everything ... now EACH and EVERY hole is a "leak" right through that wall into the sheathing, which will just rot out.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  14. #14
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Weep hole diameter

    Quote Originally Posted by Jeff Eastman View Post
    For new construction though, you tell builder to install if they don't put them in, right?

    New or old, I said "No weep holes present. Weep holes are required and needed and should be properly installed."

    That by-passes Scott's problem of "The main reason is that I don't want to be held responsible if they do not work and I told them to install them." because, *if done PROPERLY*, there will be no problem.

    How to do it "properly"? It requires brick removal by a mason and is not cheap or easy. *IF* it is discovered that there is no through-wall flashing there, then the problem just explodes bigger.

    Either way, no need to be concerned that they might come back to you, heck, if you were, you might as well quit doing home inspections, because they could come back to you for anything and everything following that scenario.

    "Do it properly." It is that simple to state. (Not always that simple to do, though.)

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  15. #15
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: Weep hole diameter

    Proper weep holes are not present in the brick veneer. Flashing is supposed to be installed behind the brick to direct water to the weep holes. I can't tell if flashing has been installed in the required areas behind the brick veneer.

    Even though some local jurisdictions require it, I seldom see proper weep holes in brick veneer in recent construction in this area. For more information on brick systems on the internet see: http://www.bia.org/html/frmset_thnt.htm Look at Technical Note #7 for weephole information.

    Also see attachment "Weep Holes In Brick Veneer". Click the link on page three of the report.

    Water does get behind brick veneer. It needs a way out so it doesn't sit in the wall rotting the structural wood until it evaporates.

    Weep holes are openings in the brick mortar that provide drainage for water (usually in vapor forn) that has penetrated into the space between the brick and the wall sheathing. When installed, these are combined with flashing (a piece of sheet metal or other similar water resistant material) between the sheathing and bricks which lead the collected moisture out the weep holes.

    There is no way to see into this space behind the brick without removing brick or opening the interior wall. Making a determination about moisture issues inside the wall is beyond the scope of this inspection.

    The Brick Industry Association (the people who make the brick and design installation requirements for it) recommend "weep holes should be located above all doors and windows, below all window sills, and above the ground at the base of the wall." Generally accepted nationwide building practices also call for proper weep holes in brick construction. However, local generally accepted building practices usually lag behind nationally accepted practices and may not require weep holes.

    Walls may be retrofitted with weep holes by drilling but this may lead to more problems as the driller usually drills straight through any flashing present giving moisture a straight shot to the structural wood. Without flashing to direct the water to the weep holes, retrofitting may be useless. Installing flashing would require removing a short span of bricks, installing flashing, putting the bricks back and doing it again and again until flashing is installed at all required locations.

    You may also want to review the following resources about the need for flashing and weep holes in brick walls.
    a. The Brick Industry Association web site at www.bia.org.
    b. An article on The Journal of Light Construction web site www.jlconline.com.
    The article is: Keeping water out of brick veneer, by Jerry Carrier. Great
    explanations, great pictures. Costs $5 to download if you're not a
    member.
    c. The Building Science Corporation web site at
    www.buildingscience.com/resources/walls/solar_driven_moisture_brick.htm
    d. Construction books at your local library.

    I recommend three courses of action:
    1. Review the above resources to educate yourself about the need for
    brick weep holes and flashing.
    2. Consult the local building inspectors office for local requirements.
    3. Contact some knowledgeable qualified brick or masonry contractors to
    determine repair methods, estimate costs, and perform the necessary
    repairs.

    Attached Files Attached Files
    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  16. #16
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Weep hole diameter

    Quote Originally Posted by Erby Crofutt View Post
    I recommend three courses of action:
    1. Review the above resources to educate yourself about the need for
    brick weep holes and flashing.
    2. Consult the local building inspectors office for local requirements.
    3. Contact some knowledgeable qualified brick or masonry contractors to
    determine repair methods, estimate costs, and perform the necessary
    repairs.
    Erby,

    #2 could backfire and work against your client if the local officials think 'weep holes are not necessary'. I would skip that one (unless I already knew that the local officials and code did require weep holes, in which case I would simply state that).

    Whether or not 'local officials' and/or 'local requirements' call for, or do not call for, weep holes, the BIA and basically anyone with any real knowledge of what needs to be done does say that weep holes are necessary.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  17. #17
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: Weep hole diameter

    Whether or not 'local officials' and/or 'local requirements' call for, or do not call for, weep holes, the BIA and basically anyone with any real knowledge of what needs to be done does say that weep holes are necessary.
    Good Point. But in Kentucky, it is illegal for me to "indicating in writing in the initial home inspection report that any condition is not in compliance with any building code enforced under KRS Chapter 198B.”"

    ====
    Kentucky Revised Statutes (KRS) Chapter 198B.738
    ”Home inspectors are prohibited from indicating in writing in the initial home inspection report that any condition is not in compliance with any building code enforced under KRS Chapter 198B.”
    ====

    I'd have to reword it to something like

    "While I can't tell you whether or not it is a code violation, ( see Kentucky Revised Statutes (KRS) Chapter 198B.738 ) the Brick Industry Association and basically anyone with any real knowledge of what needs to be done does say that weep holes are necessary."




    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  18. #18
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Weep hole diameter

    Quote Originally Posted by Erby Crofutt View Post
    Good Point. But in Kentucky, it is illegal for me to "indicating in writing in the initial home inspection report that any condition is not in compliance with any building code enforced under KRS Chapter 198B.”"

    ====
    Kentucky Revised Statutes (KRS) Chapter 198B.738
    ”Home inspectors are prohibited from indicating in writing in the initial home inspection report that any condition is not in compliance with any building code enforced under KRS Chapter 198B.”
    ====

    I'd have to reword it to something like

    "While I can't tell you whether or not it is a code violation, ( see Kentucky Revised Statutes (KRS) Chapter 198B.738 ) the Brick Industry Association and basically anyone with any real knowledge of what needs to be done does say that weep holes are necessary."


    Well, that is a stupid law! I guess you could always add an addendum to the report. Or you could say that it goes against all good building standards and guidelines.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  19. #19
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: Weep hole diameter

    Naaaaah... all you would have to do is re-issue a second report as the ammendment with the code information.

    Then, the *INITIAL* report thingy no longer applies...

    Rich


  20. #20
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Weep hole diameter

    Quote Originally Posted by Erby Crofutt View Post
    Good Point. But in Kentucky, it is illegal for me to "indicating in writing in the initial home inspection report that any condition is not in compliance with any building code enforced under KRS Chapter 198B.”
    And, as I keep pointing out, make your "initial" inspection at the front of the drive, make your "follow -up" inspection when you arrive at the house.

    That statement has such a large loop hole that you would get that new super large 800 passenger jet through it and miss the side of the loop hole by the distance between Miami and New York.

    Last edited by Jerry Peck; 06-04-2007 at 12:35 PM.
    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  21. #21
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    Erby,
    I feel your pain, but not quite as much as you do. I read the HI part of the KRS. Based on the wording, it looks like Kentucky legislators know at least as much about construction as Texas lawmaker types.

    Since I couldn't figure out how to cut and paste from pdf to here, I attached the provisions I considered most interesting.

    198B.010 It's interesting what they consider non structural.
    198B.700 They can't mean you are supposed to recommend repair methods, can they?
    198B.734 That part I like. Here in TX it's 4 years.



    Attached Files Attached Files
    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  22. #22
    Join Date
    Mar 2007
    Location
    Georgetown, KY
    Posts
    538

    Default Re: Weep hole diameter

    As I have pointed out before ( and done upon occassion) and a couple of you are now pointing out, it ain't a hard one to get around, just one I keep bitchin about cause it shouldn't be there to start with.

    Stupid laws are made everyday.

    Erby Crofutt, Georgetown, KY - Read my Blog here: Erby the Central Kentucky Home Inspector B4 U Close Home Inspections www.b4uclose.com www.kentuckyradon.com
    Find on Facebook at: https://www.facebook.com/B4UCloseInspections

  23. #23
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Weep hole diameter

    Thom, where did you get the "4 years" in Texas? I have read and re-read the TREC standards and have never found a definitive statute of limitations time frame. Can you point me in the right direction?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  24. #24
    Join Date
    Mar 2007
    Location
    Ingleside Illinois
    Posts
    118

    Default Re: Weep hole diameter

    After reading all these I have a question. I had weep holes in my walls which were filled with caulk. I pulled the caulk out and put in a piece of 3/8 cotton rope putting it in as far as possible then used clear caulk to secure the rope. Any problem with doing that ?


  25. #25
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Weep hole diameter

    Quote Originally Posted by Bill Wieczorek View Post
    After reading all these I have a question. I had weep holes in my walls which were filled with caulk. I pulled the caulk out and put in a piece of 3/8 cotton rope putting it in as far as possible then used clear caulk to secure the rope. Any problem with doing that ?
    I'd remove the rope and leave the hole open. They make a fine metal screen (kind of like brass or copper steel wool) at the very most.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  26. #26
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    Quote Originally Posted by Jim Luttrall View Post
    Thom, where did you get the "4 years" in Texas? I have read and re-read the TREC standards and have never found a definitive statute of limitations time frame. Can you point me in the right direction?
    What is in the statue is attached. What I got for an answer by phone with TREC legal was four years. I asked for citaion of statue and never received. I have sent the email below again.



    How long must an Inspector keep copies of reports from form REI 7A0 in file? Please cite statute.

    Thank you.

    Thom Walker
    Lic# 4489


    Attached Files Attached Files
    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  27. #27
    Dan Phillips's Avatar
    Dan Phillips Guest

    Default Re: Weep hole diameter

    Quote Originally Posted by Jeff Eastman View Post
    It appeared to me homeowner retrofited weep holes here along the bottom of the stone (on wood frame). The diameter of the weep holes are approximately 1 ". Any concerns with this? I know the maximum allowed is 3/8".

    That hole looks like a liquid termite treatment access.


  28. #28
    Join Date
    Mar 2007
    Location
    Corpus Christi, TX
    Posts
    615

    Default Re: Weep hole diameter

    Quote Originally Posted by Jim Luttrall View Post
    Thom, where did you get the "4 years" in Texas? I have read and re-read the TREC standards and have never found a definitive statute of limitations time frame. Can you point me in the right direction?
    Got this response this morning.

    Mr. Walker:

    There is no statutory requirement that inspectors retain copies of their reports for a specific period of time. However, because the statute of limitations on consumers filing complaints against licensees is four years, I would recommend that you keep copies of your reports for at least that long. You may also wish to consult your attorney or tax professional for advice about any other reasons you should retain copies of your records and the applicable time periods.


    We hope this information is helpful to you.

    Devon V. Bijansky
    Staff Attorney
    Enforcement Division
    (512) 465-3960
    fax (512) 465-3962







    The only reason some people get lost in thought is because it's unfamiliar territory.
    - Paul Fix

  29. #29
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Weep hole diameter

    Well, that is helpful, but they still did not cite the statue, did they?
    Thanks, Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •